Reply
 
Thread Tools Search this Thread Display Modes
 
Old 03-18-2017, 04:25 AM   #1
Commander
 
PJHoffnet's Avatar
 
Join Date: Feb 2017
Location: Merritt Island, FL
Posts: 254
Default Coming off, going on - Shore Power

OK, the excitement continues to grow for the soon 'new to me' 4100 SCA (twin diesels and a generator) 'pick up' some time next week (paper work drills continue).

So the boat will be on shore power at the current owner's slip, and I'll be heading out for a short (hour/8 nm) trip up to the marina that will be the boat's new home.

Yell at me LOUD if my thought process/procedure is wrong. Beginning with AC power coming from shore power.

Ensure both battery switches are on.

Blowers on for four minutes, bring engines and generator up. Turn off all AC loads and OPEN their breakers on panel. OPEN shore power breaker at pedestal. Shore power breaker OFF on panel, generator breaker ON. Bring back AC loads that will be running underway. Disconnect both ends of shore power cable and stow on board. Underway, blowers off after cruising speed.

Preparing to moor, blowers on. After mooring, switch off AC loads, switch off unneeded DC loads. Shut down Engines. Hook up shore power cable. AC breaker CLOSED at pedestal. Check polarity indicator GREEN. Generator breaker OPEN on panel, Shut down generator. Panel Shore Power breaker ON, bring up AC loads for in port use.

With any luck I won't blow the whole place up
__________________

__________________
Paul
Changes in L'Attitudes
1999 Maxum 4100 SCA
PJHoffnet is offline   Reply With Quote
Old 03-18-2017, 02:37 PM   #2
Admiral
 
mmwjr's Avatar
 
Join Date: Feb 2012
Location: Essex, Maryland
Posts: 10,176
Default

I think you have it down but recommend to disconnect the shore power before turning on the genny just in case you accidentally left something on and do the reverse when connecting back up.
__________________

__________________
1997 Silverton 362, 7.4 Crusaders
1997 2400 SCR, 5.7 Vortec / Bravo 2

Mike
mmwjr is offline   Reply With Quote
Old 03-18-2017, 04:50 PM   #3
Commander
 
PJHoffnet's Avatar
 
Join Date: Feb 2017
Location: Merritt Island, FL
Posts: 254
Default

Quote:
Originally Posted by mmwjr View Post
I think you have it down but recommend to disconnect the shore power before turning on the genny just in case you accidentally left something on and do the reverse when connecting back up.
Thanks Mike, good catch.
__________________
Paul
Changes in L'Attitudes
1999 Maxum 4100 SCA
PJHoffnet is offline   Reply With Quote
Old 03-18-2017, 11:34 PM   #4
Lieutenant
 
Join Date: Nov 2014
Location: Kingston ontario
Posts: 73
Default

you got this buddy. By the way, i leave my blowers on all the time when running the engines and genny
kingstonal is offline   Reply With Quote
Old 03-18-2017, 11:37 PM   #5
Lieutenant
 
Join Date: Nov 2014
Location: Kingston ontario
Posts: 73
Default

by the way Paul it never happened until you post pictures
kingstonal is offline   Reply With Quote
Old 03-19-2017, 05:12 PM   #6
Lt. Commander
 
mrt214's Avatar
 
Join Date: May 2013
Location: Pittsburgh,Pa
Posts: 175
Default

Quote:
Originally Posted by PJHoffnet View Post
OK, the excitement continues to grow for the soon 'new to me' 4100 SCA (twin diesels and a generator) 'pick up' some time next week (paper work drills continue).

So the boat will be on shore power at the current owner's slip, and I'll be heading out for a short (hour/8 nm) trip up to the marina that will be the boat's new home.

Yell at me LOUD if my thought process/procedure is wrong. Beginning with AC power coming from shore power.

Ensure both battery switches are on.

Blowers on for four minutes, bring engines and generator up. Turn off all AC loads and OPEN their breakers on panel. OPEN shore power breaker at pedestal. Shore power breaker OFF on panel, generator breaker ON. Bring back AC loads that will be running underway. Disconnect both ends of shore power cable and stow on board. Underway, blowers off after cruising speed.

Preparing to moor, blowers on. After mooring, switch off AC loads, switch off unneeded DC loads. Shut down Engines. Hook up shore power cable. AC breaker CLOSED at pedestal. Check polarity indicator GREEN. Generator breaker OPEN on panel, Shut down generator. Panel Shore Power breaker ON, bring up AC loads for in port use.

With any luck I won't blow the whole place up
Wow! When you say it like that I think I need a nap. Happy motoring.
__________________
Mike
mrt214 is offline   Reply With Quote
Old 03-20-2017, 12:47 AM   #7
Commander
 
PJHoffnet's Avatar
 
Join Date: Feb 2017
Location: Merritt Island, FL
Posts: 254
Default

Quote:
Originally Posted by mrt214 View Post
Wow! When you say it like that I think I need a nap. Happy motoring.
Tax payers' money at work - 27+ years USN Submarine service. I'm that geekwho will have a pre-underway check list, fueling che list, potable waterm loading check list, etc. I feel a lot better (safer) depending on a proven procedure in my hand than my memory.
__________________
Paul
Changes in L'Attitudes
1999 Maxum 4100 SCA
PJHoffnet is offline   Reply With Quote
Old 03-20-2017, 07:00 AM   #8
Lt. JG
 
Foxy 01's Avatar
 
Join Date: Apr 2016
Posts: 46
Default

One mechanic here claims you should always disconnect shore power before starting the engines due to the sudden overload from the alternators. Others say that is rubbish. Thoughts?
Foxy 01 is offline   Reply With Quote
Old 03-20-2017, 11:35 AM   #9
Admiral
 
mmwjr's Avatar
 
Join Date: Feb 2012
Location: Essex, Maryland
Posts: 10,176
Default

Quote:
Originally Posted by Foxy 01 View Post
One mechanic here claims you should always disconnect shore power before starting the engines due to the sudden overload from the alternators. Others say that is rubbish. Thoughts?

A boats starting and charging system are 12 VDC which is separate from shore power AC. However the battery charger is where the two can meet and IMO the charge should be turned off when starting to prevent the potential of high current being sourced from it by the starter which may result in damage to the charger. It should protect itself and limit the current draw but I would rather not put it to the test.
__________________
1997 Silverton 362, 7.4 Crusaders
1997 2400 SCR, 5.7 Vortec / Bravo 2

Mike
mmwjr is offline   Reply With Quote
Old 03-20-2017, 12:48 PM   #10
Moderator

 
shrew's Avatar
 
Join Date: Apr 2008
Posts: 5,588
Default

1) Turn off all individual AC breakers
2) Turn off main AC breakers
3) Disconnect Shore power
4) Start Engines

Why would you need to start the generator? You're only moving the boat a short distance. DC items like fridge should be able to run off of the batteries and alternator.

In reverse order:

1) Stop the engines
2) Connect shore power
3) Turn on main AC breakers
4) Turn on individual AC breakers.
shrew is offline   Reply With Quote
Old 03-20-2017, 08:30 PM   #11
Commander
 
PJHoffnet's Avatar
 
Join Date: Feb 2017
Location: Merritt Island, FL
Posts: 254
Default

Quote:
Originally Posted by shrew View Post
1)
Why would you need to start the generator? You're only moving the boat a short distance. DC items like fridge should be able to run off of the batteries and alternator.
Good point, for the marina move no need.

I was looking long term at times we would need AC for colking, etc.
__________________
Paul
Changes in L'Attitudes
1999 Maxum 4100 SCA
PJHoffnet is offline   Reply With Quote
Old 03-21-2017, 12:10 AM   #12
Captain
 
Join Date: Sep 2015
Location: Chesapeake, VA
Posts: 526
Default Coming off, going on - Shore Power

Geez, started reading your post and was expecting you to attempt to parallel the generator to the shore power bus and vice versa!
I'm a SWO, so I understand the checklist thing (although I hate them). But is it common for these bigger boats to cruise with the generator on? And turn the blower off after the engines are running! They'll just add to the noise level and decrease their life running so much.
speedysprocket is offline   Reply With Quote
Old 03-21-2017, 01:05 AM   #13
Commander
 
PJHoffnet's Avatar
 
Join Date: Feb 2017
Location: Merritt Island, FL
Posts: 254
Default

Quote:
Originally Posted by speedysprocket View Post
Geez, started reading your post and was expecting you to attempt to parallel the generator to the shore power bus and vice versa!
I'm a SWO, so I understand the checklist thing (although I hate them). But is it common for these bigger boats to cruise with the generator on? And turn the blower off after the engines are running! They'll just add to the noise level and decrease their life running so much.
You Skimmer Puke Sweater Wearing Shoe SWO Mommas and Dads don't get to have all the fun by yourselves. I used to love waching the E Div'rs watching that synchro scope spin and then close the shore power breaker hoping they were close enough to not make the bus bars bounce!

Today my wife asked if she had to use the check list even after she learned it. I almost tore up her Qual card.
__________________
Paul
Changes in L'Attitudes
1999 Maxum 4100 SCA
PJHoffnet is offline   Reply With Quote
Old 03-21-2017, 01:07 AM   #14
Captain
 
Join Date: Sep 2015
Location: Chesapeake, VA
Posts: 526
Default

Quote:
Originally Posted by PJHoffnet View Post
You Skimmer Puke Sweater Wearing Shoe SWO Mommas and Dads don't get to have all the fun by yourselves. I used to love waching the E Div'rs watching that synchro scope spin and then close the shore power breaker hoping they were close enough to not make the bus bars bounce!


Hey- I do not and will never own a SWO sweater!
And I was the Electrical Officer. Fun stuff.
speedysprocket is offline   Reply With Quote
Old 03-21-2017, 01:08 AM   #15
Lt. JG
 
Foxy 01's Avatar
 
Join Date: Apr 2016
Posts: 46
Default

Thanks Mike that makes sense.
Foxy 01 is offline   Reply With Quote
Old 03-21-2017, 12:41 PM   #16
Moderator

 
shrew's Avatar
 
Join Date: Apr 2008
Posts: 5,588
Default

Also worth noting. Very few people do this, however it is considered a best practice. Before disconnecting the shore power cord, shut off the breaker that that end is connected too. This means the breaker on the tower on the dock as well as the boat. This is especially the case if you leave your shore power cord behind on the dock. You don't want a hot cord on the dock. Especially if it rains or someone accidentally kicks it in the water.
shrew is offline   Reply With Quote
Old 03-21-2017, 03:57 PM   #17
Admiral
 
mmwjr's Avatar
 
Join Date: Feb 2012
Location: Essex, Maryland
Posts: 10,176
Default

Quote:
Originally Posted by shrew View Post
Also worth noting. Very few people do this, however it is considered a best practice. Before disconnecting the shore power cord, shut off the breaker that that end is connected too. This means the breaker on the tower on the dock as well as the boat. This is especially the case if you leave your shore power cord behind on the dock. You don't want a hot cord on the dock. Especially if it rains or someone accidentally kicks it in the water.

He captured this in the first post "OPEN shore power breaker at pedestal"
__________________
1997 Silverton 362, 7.4 Crusaders
1997 2400 SCR, 5.7 Vortec / Bravo 2

Mike
mmwjr is offline   Reply With Quote
Old 03-23-2017, 02:38 PM   #18
Captain
 
Kevlar7r's Avatar
 
Join Date: Aug 2014
Location: Jacksonville, FL
Posts: 746
Default

I also run blowers at all times. They are cheap insurance against accumulated fuel vapors, and the disastrous effect they can have.

I can not hear my blowers over the engines running, so noise is not an issue.

Yours is diesel, so somewhat less of a concern, though. But for the benefit of others who may stumble on this thread, another good habit is to open the hatch, and sniff inside the bilge. Any whiff of fuel, and don't touch the key till you've investigated and solved the issue.
Kevlar7r is offline   Reply With Quote
Old 03-23-2017, 03:17 PM   #19
Commander
 
PJHoffnet's Avatar
 
Join Date: Feb 2017
Location: Merritt Island, FL
Posts: 254
Default

Quote:
Originally Posted by Kevlar7r View Post
I also run blowers at all times. They are cheap insurance against accumulated fuel vapors, and the disastrous effect they can have.

I can not hear my blowers over the engines running, so noise is not an issue.

Yours is diesel, so somewhat less of a concern, though. But for the benefit of others who may stumble on this thread, another good habit is to open the hatch, and sniff inside the bilge. Any whiff of fuel, and don't touch the key till you've investigated and solved the issue.
I certainly couldn't hear them with the engines running. They must not have been too loud because I don't recall hearing them after shutting down. I noticed the switches on when I went back up the bridge to secure all the electronics.

You're spot on about the gas v. diesel vapor hazard. I had a Machinist Mate Chief Petty Officer who would show all the new guys how 'harmless' diesel fuel was by putting out a cig in a small cup of diesel fuel (real quick 'dunk' and kept it submerged, so little O2 or heat for the fire triangle). That being said no one should every take diesel fuel leaks or smells for granted.
__________________
Paul
Changes in L'Attitudes
1999 Maxum 4100 SCA
PJHoffnet is offline   Reply With Quote
Old 03-23-2017, 08:35 PM   #20
Lt. Commander
 
mrt214's Avatar
 
Join Date: May 2013
Location: Pittsburgh,Pa
Posts: 175
Default

I take my cord with me just in case. Also I only have 20 of the 50ft out of the boat.
__________________

__________________
Mike
mrt214 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Powered by vBadvanced CMPS v3.2.3

All times are GMT. The time now is 03:00 PM.


Powered by vBulletin® Version 3.8.8 Beta 4
Copyright ©2000 - 2024, vBulletin Solutions, Inc.